A bottomless cabinet on a larger capacity run like Bob posted is ideal situation to run all conductors of one phase in the same conduit. Ampacity adjustment does need to be considered though like he said.Even when using PVC, the steel locknut that is common to use with PVC, would have magnitization issues. So one would need to make sure to use plastic locknuts. I wasn't sure if it was non-ferrous, or non-metallic that matters.
The way I see the rules on isolated phase, it seems like it is a better practice just to avoid it all together.
Another example I've seen, is the DC equivalent of isophase. Isolated polarity installations. There is no magnetic heating that would occur, only a steady magnetic field in the conduit. I remember specifying a 1 1/4" conduit to take 6 DC conductors. It ended up getting built with two 1" conduits, and the positives in one, with negatives in the other.
If you do pass through a steel cabinet wall - a slot needs cut between openings which effectively makes them equivalent to one opening - but also need to avoid steel locknut, or you will magnetize that locknut.
I could be wrong, but other metals like aluminum, stainless, brass, copper will have some magnetic effects, but anything with iron in it will have much more of an effect.