Can I run 350 mcm paralleled in three existing 4” pvc conduits running 15ft for a total of 6 conductors per phase plus neutrals feeding a 2000amp distribution panel
 
Yes it will need an equipment ground conductor but do I need to derate the conductors if they’re parallel in the four-inch
 
That used to be one interpretation, but a few code cycles ago that was clarified, see 310.15C 1, each conductor of a parallel set shall be counted as a current carrying conductor
 
  • Ok adding three more 4”conduits and running 600mcm copper in a total of six 4” pvc conduits running 20ft for a total of 6 conductors per phase plus neutrals feeding a 2000ampbreaker after calculating 125%. Sound better?
If you're adding 3 more conduits, why not six 400mcm per phase?
 