Can I run 350 mcm paralleled in three existing 4” pvc conduits running 15ft for a total of 6 conductors per phase plus neutrals feeding a 2000amp distribution panel
If you're adding 3 more conduits, why not six 400mcm per phase?
- Ok adding three more 4”conduits and running 600mcm copper in a total of six 4” pvc conduits running 20ft for a total of 6 conductors per phase plus neutrals feeding a 2000ampbreaker after calculating 125%. Sound better?
That's what I thought at first but I think he means six conduits with one set per.So you have 12-600 kcmil conductors per phase?
Full sized ground for the circuit in each conduit.What size ground?