Parallel Generator Grounding at Generator

Status
Not open for further replies.

natfuelbill

Senior Member
Kind of a technical question, but here goes.

Not being a generator power or generator controls expert, are there any commonly known reasons why system bonding jumpers must be installed at generators?

Consider a system where grounding resistors are not used.
 

dereckbc

Moderator
Staff member
Location
Plano, TX
natfuelbill said:
Kind of a technical question, but here goes.

are there any commonly known reasons why system bonding jumpers must be installed at generators?

Consider a system where grounding resistors are not used.

I assume you mean a generator configured for an Seperately Derived System where the neutral is switched. For an SDS application the best place to bond is at the Genset as it presents the lowest impedance.

If you are considering using an impedance grounding type of genset, you really need an professional engineer making design decesions and purchases as this is specialized and requires ground fault detection, breaker coordination schemes, and equipment.
 

Natfuelbilll

Senior Member
Here is some more information.

Yes the generators are SDS.
No transfer switches are present.
No utility service is present.
Multiple generators.
Paralleling switchboard.
Prime generator power.
No grounding resistor(s) present.
SBJ can be at either the switchboard or at the generators.
Reference IEEE Orange Book

Are ther reasons why the SBJ must be at the generators and not elswhere?

If there are no grounding resistors, can the SBJ be at the generators?
 