I have a quick question on what method is used to size the grounded conductor in a parallel conduit installation for a service feeder. Knowing also that 1/0 is the minmum size that can be used, these are the two methods I would like to discuss:
Installation: (2) 4" conduits will feed 600 amp 3-phase service. Each conduit has (3) 500 kcmil ALUMINUM ungrounded phase conductors. To size the minimum grounded conductor required in EACH conduit:
Method #1 - I would take the 500 kcmil x2 for the parallel feed. Go to Aluminum column on Table 310-16, 900 kcmil thru 1750 kcmil and a 4/0 aluminum conductor is required for BOTH conduits. I would convert the 4/0 to kcmil, 211,600, divide by 2 for the two conduits and 105,800 is the size required which is a 2/0 aluminum conductor (1/0 is 105,600 and not large enough)
Method #2 - Simply look at (1) conduit no matter what size of installation. So go the the 250 thru 500 column for the (1) 500 kcmil ungrounded phase conductor and you can install a 1/0 aluminum in each conduit.
I have went thru several installation scenarios and 99% of the time either method will give you the SAME wire size except for the one above.
Any thoughts on which method should be utilized?
Thanks,
Mike
Installation: (2) 4" conduits will feed 600 amp 3-phase service. Each conduit has (3) 500 kcmil ALUMINUM ungrounded phase conductors. To size the minimum grounded conductor required in EACH conduit:
Method #1 - I would take the 500 kcmil x2 for the parallel feed. Go to Aluminum column on Table 310-16, 900 kcmil thru 1750 kcmil and a 4/0 aluminum conductor is required for BOTH conduits. I would convert the 4/0 to kcmil, 211,600, divide by 2 for the two conduits and 105,800 is the size required which is a 2/0 aluminum conductor (1/0 is 105,600 and not large enough)
Method #2 - Simply look at (1) conduit no matter what size of installation. So go the the 250 thru 500 column for the (1) 500 kcmil ungrounded phase conductor and you can install a 1/0 aluminum in each conduit.
I have went thru several installation scenarios and 99% of the time either method will give you the SAME wire size except for the one above.
Any thoughts on which method should be utilized?
Thanks,
Mike