wernerjm
New member
- Pittsburgh, PA, USA
We have a 1600A feeder that leaves the switchgear via embedded conduit (approx. 20 foot run), through a pullbox and runs in cable tray approx. 300 feet. We are running 5 parallel 3/c 5ookcmil. For the run through the tray one #4/0 is required for the EGC, but the run via conduit would need a #4/0 in each conduit. I have talked to my coworkers and have gotten different suggestions. Can I run the #4/0 in a separate conduit from the switchgear, through the pullbox and the length of the tray run? Do I need to run the separate #4/0 from the switchgear to the pullbox, terminate them, and run a single #4/0 in the tray?