mike12347 said:Infinity, How are you getting 255A with THHN
mike12347 said:Thanks guys
any opinions on 310.15(B)(2) for service entrance conductors
mike12347 said:My thought is with seperate conduits it wouldn't apply.
Agree?
In reading 310.15.(B)(6) I do not see anything that prevents this installation because of seperate conduits. What is the ampacity of the main panel?mike12347 said:My thought is with seperate conduits it wouldn't apply.
Agree?
IMO, because it does not explicitly state that we can. The rule is a fork in the road from "the normal way" of sizing conductors, with a boatload of restrictions on it.mike12347 said:My thought is with seperate conduits it wouldn't apply.
Agree?