infinity said:The total load would need to be greater than 50% non-linear for the neutral to count as a CCC. IMO this is highly unlikely. So A-B-C-N in 4 conduits would work since no derating would be required.
I agree Rob, few buildings services will need to count the neutral as a CCC.