Hi I'm wondering if someone can show me where in the NEC is allows this type of installation, where the utility connects their 4 overhead conductors (3 hot legs and 1 neutral) to the customer's 7 conductors (3 parallel sets of hot legs and one neutral) in one conduit/weatherhead feeding a meter bank. According to the Utility's requirements:
"A maximum of two (2) electrical conduits, with a maximum size of 4 inches will be permitted on a pole. Each conduit shall not be occupied by more than four (4) conductors. The conductors must be sized according to the latest edition of the National Electrical Code, NFPA 70."
So presently the Utility doesn't allow this, but I want to verify where it is shown and if exceptions are also listed. The closest article I found is 230.40, but am not certain that this is correct.
Thanks.