Hey guys we are replacing service entry wires that were stolen out of a 3P 240D system. It’s overhead drop and once through meter it lands on top of a 400A Main Breaker.
It appears that they had 500 Cu coming down to top of meter and then had 350 Cu running out of meter into main breaker. I am not sure exactly what was ran, but I DO KNOW that the load side of the meter had smaller wire then the line side, so that’s why I am assuming the 500 and 350.
First question: Is it legal to have 350 Cu powering a 400A main?????
Second question: I am not sure the breaker will accommodate 500 Cu into the lugs. They have double lugs on the line side of breaker (Siemens JXD63B400) so we were thinking of running parallels off the bottom of meter lugs. In a 3P Delta system, we DO NOT COUNT the neutral as a CCC, right? If I’m correct to that point, we could use 4/0AL from load side to breaker right?? Or can we not use 90° column for that?
Thanks in advance for any input and/or experience you guys have with this. It’s a tad out of my league in terms on common practice for this kind of stuff.
It appears that they had 500 Cu coming down to top of meter and then had 350 Cu running out of meter into main breaker. I am not sure exactly what was ran, but I DO KNOW that the load side of the meter had smaller wire then the line side, so that’s why I am assuming the 500 and 350.
First question: Is it legal to have 350 Cu powering a 400A main?????
Second question: I am not sure the breaker will accommodate 500 Cu into the lugs. They have double lugs on the line side of breaker (Siemens JXD63B400) so we were thinking of running parallels off the bottom of meter lugs. In a 3P Delta system, we DO NOT COUNT the neutral as a CCC, right? If I’m correct to that point, we could use 4/0AL from load side to breaker right?? Or can we not use 90° column for that?
Thanks in advance for any input and/or experience you guys have with this. It’s a tad out of my league in terms on common practice for this kind of stuff.