Parallel Sets of GEC

Status
Not open for further replies.

W@ttson

Senior Member
Location
NJ-USA
Occupation
PE
Suppose the GEC required is a 2/0 AWG. If you run 3 sets of #4AWG and irreversible bond both ends of the cables, would that be a code violation?
 
IMO, it would be a violation however, the code does not address this for grounding electrode conductor's. I would use 310.10(H) as a premise that doesn't allow parallel for smaller than 1/0. Again the code does not mention grounding electrode conductor's.

One can say that since the code doesn't mention it in 310.10(H) then it is not permitted to be paralleled.
 
Suppose the GEC required is a 2/0 AWG. If you run 3 sets of #4AWG and irreversible bond both ends of the cables, would that be a code violation?

If you have 3 raceways, a full size GEC is required in each raceway.
 
Some AHJs do not allow conduit to be used as a EGC's
If they haven't made a formal amendment and they are inspecting for NEC compliance they have no choice in the matter.

Roger
 
Suppose the GEC required is a 2/0 AWG. If you run 3 sets of #4AWG and irreversible bond both ends of the cables, would that be a code violation?

The answer is yes it's a violation. You need to size the GEC according to 250.66 which has no provisions for paralleling.
 
The answer is yes it's a violation. You need to size the GEC according to 250.66 which has no provisions for paralleling.


I thought I read once in the forum that the NEC is a permissive Code meaning that if it doesn't forbid it then it is allowed, or was it the opposite that I read?
 
I thought I read once in the forum that the NEC is a permissive Code meaning that if it doesn't forbid it then it is allowed, or was it the opposite that I read?
The relevant question is whether the paralleling prohibitions exclude GEC's.
 
IMO, it would be a violation however, the code does not address this for grounding electrode conductor's. I would use 310.10(H) as a premise that doesn't allow parallel for smaller than 1/0. Again the code does not mention grounding electrode conductor's.

One can say that since the code doesn't mention it in 310.10(H) then it is not permitted to be paralleled.

Good point, I choose a poor example. Suppose you paralleled 2 - 1/0 to make a 2/0 equivalent. Or you are saying since Ground Electrode conductor is not specified and only "Grounded Circuit" is listed, it cannot be paralleled?
 
250.66 says size of grounding electrode conductor, does not include "or equivalent", as is leaves this open to interpretation.

Can you use bus bar as a GEC? If so how do you size it? All that is in T250.66 is wire conductor sizes and it doesn't say "or equivalent".

Food for thought, IDK the answer.
 