Ed CarrI have two 4" rigid conduits each containing six
500mcm cu conductors. They are feeding a 3 phase
panel with a neutral. My inspector is telling me
that it may not pass. In conduit #1 I have phase A and phase B.
In conduit #2 phase C and the grounded conductor.
I have been going through my book and can't find anything
that says this is a violation. This is the service entrance
from utility transformer. Anyone?
Thanks, Ed
Hate to be the bearer of bad news, but let me give you the information as I see it.
Check 300.5(I) ex 2
Then check 300.20(B)
The installation you describe has a picture of said example in Mike Holt's "101 Essential NEC Rules" (page 128)
There are four raceways entering the bottom of the equipment. A phase in the first, B in the second, C in the third, and the N in the fourth, in what appears to be PVC.
Doesn't look good for what you are suggesting.
500mcm cu conductors. They are feeding a 3 phase
panel with a neutral. My inspector is telling me
that it may not pass. In conduit #1 I have phase A and phase B.
In conduit #2 phase C and the grounded conductor.
I have been going through my book and can't find anything
that says this is a violation. This is the service entrance
from utility transformer. Anyone?
Thanks, Ed
Hate to be the bearer of bad news, but let me give you the information as I see it.
Check 300.5(I) ex 2
Then check 300.20(B)
The installation you describe has a picture of said example in Mike Holt's "101 Essential NEC Rules" (page 128)
There are four raceways entering the bottom of the equipment. A phase in the first, B in the second, C in the third, and the N in the fourth, in what appears to be PVC.
Doesn't look good for what you are suggesting.