Smart $ said:
Ummm... while we all like to see such (i.e. when not at our expense), I assume the mention of EMT at the very beginning means the run is NOT underground.
Yes, my assumptions may be more synical, but we both are guilty of assuming.
2005 NFPA 70, 358.10 Uses Permitted
(B) Corrosion Protection Ferrous or nonferrous EMT, elbows, couplings, and fittings
shall be permitted to be installed in concrete, in direct contact with the earth, or in areas
subject to severe corrosive influences where protected by corrosion protection and judged
suitable for the condition.
According to the 2004 UL General Information for Electrical Equipment Directory
(White Book), category FJMX, galvanized steel electrical metallic tubing (EMT)
installed in concrete, on grade or above, generally requires no supplementary corrosion
protection.
Smart $ said:
Additionally, all the temp. rises you stated would put THHN conductors over the 90?C rating if the ambient temp is 30?C.
Yes, my grammer is bad, but my math is the same as last year. We looked up IEEE formulas on temp rise a few years back. You liked my results then, and I'm using the same formulas on my spreadsheet now. The label on my spreadsheet actual reads "+Temp Rise." My ambient is adjustable, currently set at 30c.