I have a client who has asked me to confirm that three shunts can be placed in parallel to measure the battery charging current for a 43KW DC array feeding a 48 volt nominal battery bank. The theoretical answer is, of course, "Yes", and the battery monitor that's been specified will properly measure amp-hours in this configuration. (FWIW, they are a large electrical contracting company located out on the west coast).
Obviously there needs to be "and be sure to have overcurrent protection for each shunt" as these are 1000 amp / 100 millivolt shunts with a maximum continuous rating of 600 amps, as I recall, but I'm not designing the system, just answering a technical question about a battery monitor.
And now for the real question -- the current through each fuse / shunt pair is inversely proportional to the resistance -- that's basic circuits. And because we're dealing with very low resistances, even a small difference in resistance will mean a large difference in current and possibly all three fuses blowing once one does. The maximum charging current is around 1,100 amps at 42 volts DC (low battery cut-off) from the array, and about 1,600 amps if they start the generator during broad daylight. The maximum continuous discharging current is around 900 amps, again at 42 volts.
Is it safe to assume that the difference in resistance between one paralleled shunt+fuse and the next is going to be small enough that even though there will be differences, they won't be so great as to blow any one fuse? Am I right in assuming that the resistance of a fuse is fairly constant for any given amperage?
Obviously there needs to be "and be sure to have overcurrent protection for each shunt" as these are 1000 amp / 100 millivolt shunts with a maximum continuous rating of 600 amps, as I recall, but I'm not designing the system, just answering a technical question about a battery monitor.
And now for the real question -- the current through each fuse / shunt pair is inversely proportional to the resistance -- that's basic circuits. And because we're dealing with very low resistances, even a small difference in resistance will mean a large difference in current and possibly all three fuses blowing once one does. The maximum charging current is around 1,100 amps at 42 volts DC (low battery cut-off) from the array, and about 1,600 amps if they start the generator during broad daylight. The maximum continuous discharging current is around 900 amps, again at 42 volts.
Is it safe to assume that the difference in resistance between one paralleled shunt+fuse and the next is going to be small enough that even though there will be differences, they won't be so great as to blow any one fuse? Am I right in assuming that the resistance of a fuse is fairly constant for any given amperage?