petersonra
Senior Member
- Location
- Northern illinois
- Occupation
- Semi-retired engineer
I have always thought it was curious as well.
It appears that CMP6 does not agree....What I do object to is the attempt to apply the same reasoning to the use of a pair of 1/0 for a 350 amp feeder to an individual dwelling unit, by doubling the "ampacity" value in Table 310.15(B)(6).
6-74- (Article 310, Notes to Ampacity Tables of 0 to 2000 Volts, Note 3): Reject
SUBMITTER: R.W. Worthing, Auberry, CA
RECOMMENDATION: Add new text at the beginning of the second sentence to read:
Application of this Note shall not be permitted for conductors connected in parallel.
SUBSTANTIATION: At a recent Section meeting of the 1AEI, the question of the applicability of Note 3 to parallel conductors was raised. No consensus was established. Actions, by CMP 6, whether in acceptance or rejection of this Proposal, will establish, for the record,the position of the Panel.
PANEL ACTION: Reject.
PANEL STATEMENT: Conductors 1/0 and larger are permitted to be paralleled by Section 310-4. This would apply to Note 3.
NUMBER OF PANEL MEMBERS ELIGIBLE TO VOTE: 10
VOTE ON PANEL ACTION:
AFFIRMATIVE: 10
You have to go back to the 93 code, this was a proposal for the 96 code. What was note 3 is now 310.15(B)(7).Before I say why I disagree that they disagree, or why it is not relevant that they might disagree, can you tell me where these alleged "notes to ampacity tables" might be? I cannot figure out what the proposal meant, or what their rejection meant, without seeing the original text. But I don't see any notes to Table 310.16.
I guess he said it better than I did or you just don't like me... :weeping:I like this. Thanks.
I guess he said it better than I did or you just don't like me... :weeping:![]()
Based on the proposal and panel comment, it is clear to me that the panel intends to let us use two sets of 2/0 copper for a 400 amp dwelling unit service. I don't see how you can read the proposal any other way.
Assuming they are not in the same raceway, what logic would say that a cable with an ampacity of 335 amps is better than two cables with a combined ampacity of 350 amps for a 400 amp dwelling unit service.
I do see the proposal your way.
I also think they are wrong as the words in the NEC do not support it in my opinion.
The problem with the panel statement is that it does not give a complete answer. They say that we can parallel conductors, and we already knew that. But what happens when we parallel conductors is never spelled out anywhere (not even in the ampacity tables), and this is one place where it should be spelled out. All I would ask is that the word "ampacity" be inserted somewhere in the table. As an alternative, a statement should be added to declare that two parallel conductors of the tabulated size can be used for a service of twice the tabulated rating.
I usually caution that titles are not part of the Code itself; however, occasionally they are a reasonable basis for interpretations. As such, with the overall Section 310.15 titled Ampacities for Conductors Rated 0?2000 Volts, it would seem that Section 310.15(B)(7) is a description of the basic conductor ampacity for a very specific ?condition of use?.
The problem is there is no statement directly or by reasonable subordination to another Section in either the Section 310.15(B)(7) text or table for the ambient that was used to determine the Table ampacities. Therefore, there is no basis for corrections or adjustments based on different ambient conditions. Other adjustments not based on ambient conditions, such as more than three current carrying conductors in a raceway or cable, would still apply.
In my opinion, each member of a properly installed parallel conductor has "full" ampacity subject to the appropriate adjustments and corrections.
Hopefully this is better:I would agree or disagree if I was smart enough to understand what you just wrote, but I am not.
Got a dummy version for us grunts?