Due to many large trees being in the Way and cost, Primary power was not sent to the back of a farm to keep Secondary 240 volt supply close to the area needing Electrical Service.
The voltage drop calculation for 160amp on each conductor calls for Parallel #750 kcmil Aluminum for the 430' run. I have looked at Transforming to 600 volts and drop back down to 240 volts at the Load end, but the cable would still need to be 4/0 aluminum and the Transformers are expensive for that single phase voltage that will take time to build and ship to Site. If we used #750 kcmil paralleled to supply an 80% load of 320amps, would there be issues with voltage drop even when using such large cable? At that distance I could see a lot of line loss at 240 volts?
Thanks for your feedback!
The voltage drop calculation for 160amp on each conductor calls for Parallel #750 kcmil Aluminum for the 430' run. I have looked at Transforming to 600 volts and drop back down to 240 volts at the Load end, but the cable would still need to be 4/0 aluminum and the Transformers are expensive for that single phase voltage that will take time to build and ship to Site. If we used #750 kcmil paralleled to supply an 80% load of 320amps, would there be issues with voltage drop even when using such large cable? At that distance I could see a lot of line loss at 240 volts?