Lcdrwalker
Senior Member
- Location
- Columbus, Ohio
I have some AHJ's give me conflicting answers to the following installation.
When we install parking lot lighting, we install a ground ron and #6 bare conductor bonded to the pole. Some AHJ'S require we bond our equipment grounds to the #6 and others will not permit it. Comments?
The way that it has been explained is that the #6 is concidered to be for lightning protection. What didn't make sense to me is that the #6 is bonded to the pole at the factory supplied lug in the pole base where the EG runs to the top of the pole at the ballast. I will agree that they are interconnected through the metal parts of the head(s) and the pole.
When we install parking lot lighting, we install a ground ron and #6 bare conductor bonded to the pole. Some AHJ'S require we bond our equipment grounds to the #6 and others will not permit it. Comments?
The way that it has been explained is that the #6 is concidered to be for lightning protection. What didn't make sense to me is that the #6 is bonded to the pole at the factory supplied lug in the pole base where the EG runs to the top of the pole at the ballast. I will agree that they are interconnected through the metal parts of the head(s) and the pole.