So the job I'm on is not requiring inline fuses at the handhole for it's parking lot light poles. I had always thought this was required but it seems it's only required for street lighting? That's my first question.
Secondly, as I was looking through the NEC for this very problem it seemed that under 410.8 and 410.130(G)(1) the inline fuse not only served as protection of the individual light pole but also as it's disconnecting means, and without the fuse the poles would have neither individual overcurrent protection or a disconnecting means required for inspection. Also, the EGC is not bonded to the pole, there is a seperate "bonding jumper" that terminates at the handhole and at the top of the pole and at no point connects to the EGC. It also does not travel with the branch circuit conductors, it originates at the pole which I find odd.
Thanks for the opinions!
Secondly, as I was looking through the NEC for this very problem it seemed that under 410.8 and 410.130(G)(1) the inline fuse not only served as protection of the individual light pole but also as it's disconnecting means, and without the fuse the poles would have neither individual overcurrent protection or a disconnecting means required for inspection. Also, the EGC is not bonded to the pole, there is a seperate "bonding jumper" that terminates at the handhole and at the top of the pole and at no point connects to the EGC. It also does not travel with the branch circuit conductors, it originates at the pole which I find odd.
Thanks for the opinions!