I was called out to troubleshoot a tripping breaker for parking lot lighting. The the 50A breaker when reset and the load switched on would hold for about 20 seconds. I measured 130A during this time. The metal poles are powering 1000w lamps at 480v. One of the lines for a single lamp had faulted to the inside of the metal pole. It may have been a high impedance fault and/or the egc may have also had some poor connections. The pole was about 500' from the source.
I am assuming the fault current took parallel paths back to the source on the egc and through earth.
After repairs were made and while debriefing the maintenance staff it was asked if the pole was energized during the fault. My response was that the system operated properly to clear the fault. There was likely some voltage between the pole and ground but that it would be very small and definitely not the full system voltage.
Do you think any hazardous voltage could have been present from the pole to ground during the fault?
I am assuming the fault current took parallel paths back to the source on the egc and through earth.
After repairs were made and while debriefing the maintenance staff it was asked if the pole was energized during the fault. My response was that the system operated properly to clear the fault. There was likely some voltage between the pole and ground but that it would be very small and definitely not the full system voltage.
Do you think any hazardous voltage could have been present from the pole to ground during the fault?