Parking lot pole lights

Status
Not open for further replies.

benaround

Senior Member
Location
Arizona
Does the NEC require grounding electrodes installed at parking lot pole lights per 250.32.
Aside from the exception,of course.
 
Re: Parking lot pole lights

Originally posted by benaround:
Does the NEC require grounding electrodes installed at parking lot pole lights per 250.32.
Aside from the exception,of course.
IMO yes, if the pole is supplied by a feeder or more than one branch circuit.

That said I don't think they will do anything. ;)
 
Re: Parking lot pole lights

In this exact case, I would use my enforcement authority expressed in the second paragragh of 90.4 and grant special permission not requiring a separate electrode at each pole, especially where these poles are effectively grounded by attachement to a concrete base underground.
 
Re: Parking lot pole lights

Some people claim that a ground rod at each pole will provide some benefit in the event of lightning activity. True or no? Is it your (Bryan's) contention that the pole J-bolts and the concrete base are already pretty much a Ufer gound, making any ground rods redundant?
 
Re: Parking lot pole lights

Thanks for the replies Bob,Bryan,and Dr. Shunk.

I have noticed latley that the pole light details no longer include the electrode (rod) so it must be the 'new' way of thinking about it.
A few years ago we were cad welding what we no longer even need?
 
Re: Parking lot pole lights

Originally posted by mdshunk:
Some people claim that a ground rod at each pole will provide some benefit in the event of lightning activity. True or no?
In my opinion NO.

Is it your (Bryan's) contention that the pole J-bolts and the concrete base are already pretty much a Ufer gound, making any ground rods redundant?
In my opinion YES.
 
Re: Parking lot pole lights

From Bryan

"In this exact case, I would use my enforcement authority expressed in the second paragragh of 90.4 and grant special permission not requiring a separate electrode at each pole, especially where these poles are effectively grounded by attachement to a concrete base underground."

You do not need to use 90.4, you can reference 250.54
 
Re: Parking lot pole lights

Originally posted by georgestolz:
What about 250.32(A), exception?
That certainly does seem to apply.

There are rare circumstances in which you'll have more than one circuit to a pole light. I did some pole lights near a helicopter landing pad that had a second circuit for flashing red lights on top. I did some that had a receptacle about 6 feet down from the shoeboxes for lighted holiday wreath thing-a-ma-jigs that were a seperate circuit.

Even if not expressly required, I will continue to put a ground rod at pole lights for the purpose of shunting some of a lightning strike to earth right at the pole. Even if it is just superstition, it makes me feel better to do so.
 
Re: Parking lot pole lights

George,

In my O.P. I set the exception aside. Consider more than one circuit, and not multi wire.

Frank
 
Re: Parking lot pole lights

The equipment bonding conductor provides the ground fault return path, that is all that is required. The ground rod serves no purpose.

romeo
 
Re: Parking lot pole lights

Originally posted by romeo:
The equipment bonding conductor provides the ground fault return path, that is all that is required. The ground rod serves no purpose.

romeo
Romeo, I agree they would serve no purpose.

However if they are served by more than one branch circuit or a feeder then 250.32(A) requires grounding electrodes.
 
Re: Parking lot pole lights

A light pole does not require a disconnect. A code change several cycles ago clarifed this.
See 225.32 Exception 3
 