IMO yes, if the pole is supplied by a feeder or more than one branch circuit.Originally posted by benaround:
Does the NEC require grounding electrodes installed at parking lot pole lights per 250.32.
Aside from the exception,of course.
In my opinion NO.Originally posted by mdshunk:
Some people claim that a ground rod at each pole will provide some benefit in the event of lightning activity. True or no?
In my opinion YES.Is it your (Bryan's) contention that the pole J-bolts and the concrete base are already pretty much a Ufer gound, making any ground rods redundant?
That certainly does seem to apply.Originally posted by georgestolz:
What about 250.32(A), exception?
Romeo, I agree they would serve no purpose.Originally posted by romeo:
The equipment bonding conductor provides the ground fault return path, that is all that is required. The ground rod serves no purpose.
romeo