We have a 480V 3 phase wye delta motor contactor controlling a motor. The drawing calls for a parallel feed to be brought from the mcc to the main contactor and then jumpered over to the delta contactor. The contractor is saying that he will bring one set of the parallel feeder to the main contactor and the other set to the delta contactor. He will then put a jumper between contactors.
I don't believe that you can do this and am trying to explain why. The first thing that comes to mind I'd the fact that parallel feeders need to land on the same termination point and not on seperate contactors (even I jumpered)
Besides what I mentioned above are there other reasons why this cannot be done this way?
I don't believe that you can do this and am trying to explain why. The first thing that comes to mind I'd the fact that parallel feeders need to land on the same termination point and not on seperate contactors (even I jumpered)
Besides what I mentioned above are there other reasons why this cannot be done this way?