Situation is two new electric vented skylights that come supplied with 20' 14-2 romex prewired whips. If the only branch circuit available in the attic is a 20 amp, can I place a 15 amp fuse in a JB to protect the skylights on the 20 amp circuit? It seems that this is not a tap since the conductors are protected at their source of supply. The only other choices I see are to change the entire circuit to 15 amp (confusing) or run a HR to the panel (PITA).