Partial Discharge testing

Merry Christmas
Status
Not open for further replies.

JdoubleU

Senior Member
Is anyone out there doing routine partial discharge testing on there medium voltage cables. We had one done 7 years ago on ours but I feel a new one needs to be done now. I am seeking advice on how often others are doing there if anyone is. The company recommends every 3 years.
 
Most places I've been involved with for underground power or HV radar (e.g 3 mW, 11kV 60 Hz; or a few hundred kW at 40 kVdc) only do a PD test initially, then run the system till there is a failure. Overhead lines mostly have RF detection from the ground on a routine (annual) basis mostly to detect contaminants on the insulators.

There is a French company that has a charge/relaxation test that can predict remaining lifetime in XLPE cables. I'll post a link if I can find any open source data on-line, details in my files from a visit to the folks doing that work at Marseille a few years ago may not have been made public yet.
 
The frequency is related to equipment reliability requirements and equipment age / condition. If both are average, the NETA testing frequency for MV cables is every 3 years for electrical testing procedures.
 