- Occupation
- Electrical Contractor, Electrical Consultant, Electrical Engineer
Here,
Assume all the connections are tight and solid.
Think of the source voltage at the secondary terminals of the PoCo transformer. There's 240V (or some higher voltage) from line (L1) to line (L2) and 120V line to center tap.
Put the motor out on the end of 371' of conductor (one way).
As the 70A start current flows around line L1 and the grounded conductor connected to the center tap, the 120V at the xfmr will decrease by the voltage drop of the line conductor resistance times the current.
At the same time, the 70A start current returning to the xfmr center tap will cause a voltage rise toward the line L1 further decreasing the load voltage at the saw motor.
The brightening of lights on the L2 side comes from the voltage on L2 not changing while the grounded conductor and (after the service disco) the neutral voltage rise moves away from L2 towards L1.
Assume all the connections are tight and solid.
Think of the source voltage at the secondary terminals of the PoCo transformer. There's 240V (or some higher voltage) from line (L1) to line (L2) and 120V line to center tap.
Put the motor out on the end of 371' of conductor (one way).
As the 70A start current flows around line L1 and the grounded conductor connected to the center tap, the 120V at the xfmr will decrease by the voltage drop of the line conductor resistance times the current.
At the same time, the 70A start current returning to the xfmr center tap will cause a voltage rise toward the line L1 further decreasing the load voltage at the saw motor.
The brightening of lights on the L2 side comes from the voltage on L2 not changing while the grounded conductor and (after the service disco) the neutral voltage rise moves away from L2 towards L1.