brycenesbitt
- United States
A project I'm working on received a correction notice. Would others comment?
The situation was: the project added a new subpanel, with the old fuse box turned into a junction box for two remaining old knob & tube circuits running lighting.
Late in the project it became clear something was wrong. Apparently at some point in the past the knob & tube neutral had been severed, and someone (likely not a professional) sponged a neutral from a wildly different subpanel. That lead to a potential double neutral situation of two circuits on the same phase using the same neutral.
Two solutions were considered, and option B was implemented by the electrician on the project:
I was note on site: but the crew tells me the City inspector was concerned seeing the neutrals heading in two directions, out of concern that it was a double neutral.
So now the question is try a different solution, or try to explain this to the inspector?
What do your AHJ's have you do when needing to patch knob and tube (here we generally are allowed to use the old methods on the old wires, including running modern wire through tubes when cleaning up old crap work on knob & tube).
Not pass - at attic: single connections to existing knob&tube wiring must follow 2019
CEC article 394, 300 & 314 as required, wiring must be properly protected and secured
(see pics for current location/condition)- call for reinspection
![ktpatch.jpg ktpatch.jpg](https://forums.mikeholt.com/data/attachments/25/25252-f73d90dad0a7fcc56ee9ff96d13236b9.jpg)