anbm

Senior Member
Location
TX
Occupation
Designer
We have (2) separate buildings belong to same owner, there is a open walk way connecting two buildings, each building has 6 stories. Landscape architect have designed some MH lights along the walk way. And they asked if any codes require that we need to provide emergency lights along this path and what minimum foot-candle need to achive when on emergency power (generator)? (1 Foot-candle?), building has generator but it will take sometime to have those MH lights (on generator if needed) to be on after loosing normal utility power.
 
you're only required to provide emergency lighting along the path of egress to a safe distance from the building.

If you need the MH fixture as an emergency fixture on generator then you can either install a quartz restrike, arc keeper, or install a non-MH fixture that has instant on capability.
 