There is a new lighting system out that operates on 70V. They make them in cans and lay-in form. It has a xfmer that mounts onto a 4 square box above the light (at line voltage). The current is very low. Juno modu-lites are the name. There is then a nm jacketed cable (looks similar to a CAT 5 from the outside, never opened one up) and it plugs into the module (xfmer). The argument is the Rep says it can be placed in a patient care area because of the voltage (being a class I or II I don't remember which). I say it must comply with 517.13 (A) and (B). Under other conditions, it is supported by j-hooks or rings like data cables.
He is trying to say since it is less than 100 volts it doesn't have to have a metallic sheath or raceway listed as a ground fault return path. My case is it doesn't matter. The only exception is you may omit the insulated EGC where over 7 1/2' and where switches are are located outside the patient care area.
His position is due to the class, it does not have to comly nor is a lighting fixture fixed equipment. My case is if a fixture is not fixed equipment, luminares would not be mentioned in exception no.2. Any thoughts?
[ November 26, 2005, 06:45 PM: Message edited by: necbuff ]
He is trying to say since it is less than 100 volts it doesn't have to have a metallic sheath or raceway listed as a ground fault return path. My case is it doesn't matter. The only exception is you may omit the insulated EGC where over 7 1/2' and where switches are are located outside the patient care area.
His position is due to the class, it does not have to comly nor is a lighting fixture fixed equipment. My case is if a fixture is not fixed equipment, luminares would not be mentioned in exception no.2. Any thoughts?
[ November 26, 2005, 06:45 PM: Message edited by: necbuff ]