I would first like to thank everyone that may post on this thread...
We have been doing more and more of Doctor and Patient care facilities in the past few years. I have some questions about why and if we are installing the redundant ground correctly.
Recently we have had a few new out of state emplyees that have raised some questions of why we are installing a redundant ground MC cable and that they have never used such a thing when they worked on similar installations. (this is something that I look at closely but dont put too much weight to as to they could have been doing it wrong)
The 2 NEC sections that I am looking at is 517.113 (A) & (B) and 250.118. Also, I am utilizing a NEC 2005 hard cover handbook which has more info then a standard NEC code book.
We are currently intalling EMT brach circuits runs to Junction boxes then roping the walls in any patient care area i.e. examination rooms, rest rooms, waiting areas, therapy rooms with a 12-2, 12-3 green MC cable it has #12 conductors #12 grounded conductor #12 Equipment grounding conductor (green) and a aluminum wire which looks to be smaller than #14 as a redundant ground. This aluminum that is running thru the cable we take and turn back on itself at least 3 turns on the outside of the MC, per instruction from the manufaturer.
So now starting at
517.3 (A) Wiring Methods All branch circuits serving patient care areas shall be provided a with a ground path for fault current by the installation in a metal raceway system, or a cable having a metallic cable armor, or sheith assembly shall itself quallify as an equipment grounding return path in accordance with 250.118
(B) Insulated Equipment Grounding Conductor the ground terminals of all receptacles and all non-current carrying conductive surfaces of fixed electric equipment likely to become energized that are subject to personal contact, operating at over 100 volts shall be grounded by an insulated copper conductor. The equipment grounding conductor shall be sized in accordance with 250.122 and installed in a metal raceway or as part of listed cables having a metallic armor or sheith assembly with the branch circuit conductors supplying these receptacles or fixed equipment.
In a standard code book there is no use of the word REDUNDANT. So a person may think that a standard MC having a green equipment conductor in both instance (A) and (B) would be sufficent. But looking at the wording under the header of 517.13 it states "Wiring in patient care areas shall comply with 517.13(A) AND 517.13(B)." The "AND" being the key word there. That is where it should be understood the redudency comes from.
So under the (A) section if you were to comply with all 250.118 (5) a-d you could infact utilize a MC cable. I however am not sure if the MC connectors are listed for grounding and most of the installations we do the MC runs are longer than 6ft. so this blows that exception out of the water for us.
I would like some input to make sure we are doing correct install or if anyone is doing anthing diffrent that I have not looked at. I have never had an inspector call me on any portion of our istallation in Patient care areas. (bummer is that some have asked why we were installing the green MC.)
We have been doing more and more of Doctor and Patient care facilities in the past few years. I have some questions about why and if we are installing the redundant ground correctly.
Recently we have had a few new out of state emplyees that have raised some questions of why we are installing a redundant ground MC cable and that they have never used such a thing when they worked on similar installations. (this is something that I look at closely but dont put too much weight to as to they could have been doing it wrong)
The 2 NEC sections that I am looking at is 517.113 (A) & (B) and 250.118. Also, I am utilizing a NEC 2005 hard cover handbook which has more info then a standard NEC code book.
We are currently intalling EMT brach circuits runs to Junction boxes then roping the walls in any patient care area i.e. examination rooms, rest rooms, waiting areas, therapy rooms with a 12-2, 12-3 green MC cable it has #12 conductors #12 grounded conductor #12 Equipment grounding conductor (green) and a aluminum wire which looks to be smaller than #14 as a redundant ground. This aluminum that is running thru the cable we take and turn back on itself at least 3 turns on the outside of the MC, per instruction from the manufaturer.
So now starting at
517.3 (A) Wiring Methods All branch circuits serving patient care areas shall be provided a with a ground path for fault current by the installation in a metal raceway system, or a cable having a metallic cable armor, or sheith assembly shall itself quallify as an equipment grounding return path in accordance with 250.118
(B) Insulated Equipment Grounding Conductor the ground terminals of all receptacles and all non-current carrying conductive surfaces of fixed electric equipment likely to become energized that are subject to personal contact, operating at over 100 volts shall be grounded by an insulated copper conductor. The equipment grounding conductor shall be sized in accordance with 250.122 and installed in a metal raceway or as part of listed cables having a metallic armor or sheith assembly with the branch circuit conductors supplying these receptacles or fixed equipment.
In a standard code book there is no use of the word REDUNDANT. So a person may think that a standard MC having a green equipment conductor in both instance (A) and (B) would be sufficent. But looking at the wording under the header of 517.13 it states "Wiring in patient care areas shall comply with 517.13(A) AND 517.13(B)." The "AND" being the key word there. That is where it should be understood the redudency comes from.
So under the (A) section if you were to comply with all 250.118 (5) a-d you could infact utilize a MC cable. I however am not sure if the MC connectors are listed for grounding and most of the installations we do the MC runs are longer than 6ft. so this blows that exception out of the water for us.
I would like some input to make sure we are doing correct install or if anyone is doing anthing diffrent that I have not looked at. I have never had an inspector call me on any portion of our istallation in Patient care areas. (bummer is that some have asked why we were installing the green MC.)