tshea Senior Member Location Wisconsin May 26, 2005 #1 We know about redundant grounds for switches and receptacles in patient exam rooms. What about the light fixtures on a 9' ceiling?
We know about redundant grounds for switches and receptacles in patient exam rooms. What about the light fixtures on a 9' ceiling?
rcarroll Senior Member Location Fort Collins, Colorado May 26, 2005 #2 Re: Patient exam rooms The definition of patient vicinity in 517 extends vertically not less than 7.5' above the floor. I hope this is what you are looking for. Ron
Re: Patient exam rooms The definition of patient vicinity in 517 extends vertically not less than 7.5' above the floor. I hope this is what you are looking for. Ron
sandsnow Senior Member Location Southern California May 26, 2005 #3 Re: Patient exam rooms It's here. 517.13(B) EX 2