5000w patio heater on a 30 amp, 240v breaker has two heating elements(each element rated at half nameplate of heater). Manufacture provided a dual toggle switch and shows L2 going straight to one side of both heating elements while L1 gets pigtailed and landed on inputs of each switch. Instructions then say to refer to tap rules and suggest coming off the load side of the switches with #12 to each heating element.
Do the tap rules allow this? I thought any tap conductor was supposed to land on an OCPD?