A Alwayslearningelec Senior Member Location NJ Occupation Estimator Monday at 3:32 PM #1 If I have a straight pull with (5) 4" conduit is it just 8x4 or I need to add something for the additional conduits? Thanks
If I have a straight pull with (5) 4" conduit is it just 8x4 or I need to add something for the additional conduits? Thanks
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Monday at 3:43 PM #2 8 X 4 but I wouldn't use that minimum size if you're splicing.
A Alwayslearningelec Senior Member Location NJ Occupation Estimator Monday at 4:02 PM #3 infinity said: 8 X 4 but I wouldn't use that minimum size if you're splicing. Click to expand... No splice. Bu that just gives you which wall dim? THe length. What about height an depth?
infinity said: 8 X 4 but I wouldn't use that minimum size if you're splicing. Click to expand... No splice. Bu that just gives you which wall dim? THe length. What about height an depth?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Monday at 4:04 PM #4 Only needs to be deep enough to get the locknuts and bushings on. For 4" typically 6" minimum 8" would be better.
Only needs to be deep enough to get the locknuts and bushings on. For 4" typically 6" minimum 8" would be better.