I have been handed the task to fix an issue where someone has designed, built and installed a control panel.  When the inspector came in to inspect he would not approve the installation.  I was first informed that the breaker feeding the control panel had a short circuit rating of 36KA and the main breaker in the panel has a short circuit rating of 18KA and this was the problem.  This made absolutely no sense and upon further questioning I finally got that the inspector wants to see the calculation showing the Peak Let-through Current of the 18KA Main breaker and whether or not the branch circuits downstream and starter assembly's (rated 42KA) are capable of withstanding the let through current.
The panel consists of a Main breaker (300A, Isc=18KA) with three branch breakers ((100A, Isc=18KA), (100A, Isc=18KA), (20A, Isc=18KA)) and a set of fuses (10A, Class J)
To make this short and simple I have no idea how to determine the peak let-through current and I am looking for a little help and/or guidance on how to go about this.