physis

Senior Member
I tried to find a resolution to this but I failed.

A peninsular counter requires 1 receptacle. Right?

Can this receptacle be one that also serves the counter? This peninsula butts right into a wall/counter intersection with an outlet.
 
Re: Peninsula counter receptacle

Maybe...If you have anything in the peninsular/island countertop, cooktop, sink, refrig, etc, then you have 2 spaces and will need a recept in each space unless the countertop extends more than 6" beyond it's base. It can come off the countertop circuit or any other small appliance branch circuit of 210.11 (C)(1) and 210.52 (B)(1-5). I don't think the countertop recept at the intersection you speak of satisfies the intent of the code. You still have to consider the lenth of wall space. If the peninsular is less than 2' you may can get away with it.

[ August 15, 2004, 04:34 PM: Message edited by: necbuff ]
 
Re: Peninsula counter receptacle

The 24 inch deep counter that is against the wall is one counter space by it's self and requires a receptacle. The peninsula that butts up against that counter, is a separate counter space and is required to have it's own receptacle.
 
Re: Peninsula counter receptacle

210.52(B)(3): At leat one receptacle outlet shall be installed at each peninsular counter space with a long dimension of 24" or greater and a short dimension of 12" or greater. A peninsular countertop is measured from the connecting edge.

I guess the question lands on "at". Is the counter receptacle "at" the peninsula?

Editted misspell.

[ August 15, 2004, 04:52 PM: Message edited by: physis ]
 
Re: Peninsula counter receptacle

If the penninsular is unbroken by sinks/cooktops etc. then only one required.Good practice would have more if a long penninsular,JMHO ;)
 
Re: Peninsula counter receptacle

If the peninsula is unbroken by.....,and if the distanc from where the peninsula meets the cntr. edge and its end is less than 2'---the you don't need the recpt at end--
 
Re: Peninsula counter receptacle

Necbuff:
then you have 2 spaces and will need a receptacle in each space unless the countertop extends more than 6" beyond it's base.
With the wording you provided, it could be very misleading, such as if you have a countertop space with a larger then 6" overhang on the back side and on the end, we don't need a receptacle?
 
Re: Peninsula counter receptacle

We do pilot inspections before they go into full production. They had roughed in the recep on the end of the peninsula. They had to construct the counter so that it met the 6 inch reqment.
Architectural design does not supercede the NEC, though architects and designers may disagree ;)
 
Re: Peninsula counter receptacle

Russ, I'm looking at your take on it and I tend to agree. But wouldn't the interpretation come out differently if the intersection were a 45 degree and the peninsula actually contacted the wall?
 
Re: Peninsula counter receptacle

physis

I would tend to go with the depth of the rest of the counter space along the same wall. What ever extended out beyond that I would consider the peninsula.
 
Re: Peninsula counter receptacle

On this one the GC put a 4' high wall behind the peninsula. The length was over 6'. I installed 2 receptacles on the peninsula and on the other side of the wall I installed 1 for 210.52(A)(2)(1)(a subsection with a subsection). Before the wall was going to be installed I was just scratchin my chin wondering if it would work. You guys seem somewhat unanymous I'm not getting far with this.

Can I invoke the "it's to hard I don't have to rule"?
 
Re: Peninsula counter receptacle

VOLT101,
" IT COULD BE MISLEADING"
That reference was made regarding an island/peninsula that has a 6" overhang on all sides. There would be no legal place to install the recptacle.
 
Re: Peninsula counter receptacle

The general rule is that the receptacle is to be mounted above. With the exception, it could be permitted to be installed below, only if the over hang is less then 6", but if it is more, then it is simply not permitted to be there. The exception here does not waive the code article in this case. The receptacle is still required.

So a tombstone would be required.
 
Re: Peninsula counter receptacle

Ok what about one inside the cabinet,front side and within required measurments.front I mean the door side nothing in the NEC prohibits this installation as far as I can see(have been allowed in a condo complex)It`s accesible,less than 6 ins. of overhang and if placed right within 8 ins. of the countertop.It amazes me that a plan can be approved by the EI and tagged on installation.sure the disclaimer is there,but why approve it ??????
 