Anyone have experience on a large project where you utilized permanent switchgear/feeders for temporary power/lighting?
It's done all the time. What are you trying to find out?Anyone have experience on a large project where you utilized permanent switchgear/feeders for temporary power/lighting?
It's done all the time. What are you trying to find out?
Thanks.We use as much permanent stuff for temp that we can during new construction. At times it can be problematic because when the time comes to use those temp risers for permanent power often you're still using them for temp power which creates other issues. Given a choice I would just run temp MC risers which can be cut, redirected and altered much more easily as permanent power becomes available.