This would be a rare installation for either type of pool. However if you have a permanently installed pool with the water level 2' or less above the surrounding surface 680.26(B)(2) applies.
(2) Perimeter Surfaces.
The perimeter surface to be bonded shall be considered to extend for 900 mm (3 ft) horizontally beyond the inside walls of the pool while also at a height between 900 mm (3 ft) above and 600 mm (2 ft) below the maximum water level. The perimeter surface shall include unpaved surfaces, concrete, and other types of paving....
Where did you get that from. I am not seeing the bold part in 2017, 2020 or 2023. At least not in 680.26(B)(2)
I think you maybe are thinking about it backwards? Bold part above wherever it came from means the perimeter surface that needs bonded is within 3 feet horizontally from inside pool wall and any surface less than three feet above the max water level or less than two feet below max water level.But it's backwards - the further the distance the more safety is required...
If you have a 42 inch high wall on a freestanding pool it is more than 2 feet to the ground from max water level unless you place some other surface alongside the pool like a deck. In that case it is a longer reach for a pool user between the two points. IMO is more of a danger if you are inside the pool and reaching out to some other surface not at same potential than if standing outside the pool and reaching in. But with a 42 inch high side wall it would be difficult for most people to reach the ground while standing in the pool. Being able to reach two feet below the max water level on the outside of the pool seems pretty likely for most people that are over age ~12 anyway.