Here is the photo client sent, buyer says that it is on the same circuit of the SA, but seller says it is according to 1991. Jees, what a torment for few pennies ... I will check tomorrow, but I don't want spending time on this.
Sorry, what is SOL as beating the seller? English is my second language and sometimes and don't get idiomatic expressions.
Realtor sent a message stating that the microwave is in the kitchen light circuit. I really hate those cheapers that hire handymen to remodels and later cry when found those errors.
I have a quotation in my business cards that read: "if you think it's expensive to hire a professional to do the job, wait until you hire an amateur"
So, now after everything is closed it will cost money to run the circuit as the buyer wants it directly from the panel.
I tried to saved money for the seller and this is why I tried to go for the old code, but if it is in the light circuit ... Forget it
Please , I would like your opinions about this multiwiring in same phase for 26 years, can it be possible that nothing happened on those 26 years?
(2) Utilization Equipment Fastened in Place. The total
rating of utilization equipment fastened in place, other than
luminaires, shall not exceed 50 percent of the branchcircuit
ampere rating where lighting units, cord-and-plugconnected
utilization equipment not fastened in place, or
both, are also supplied
Hi user 100, I mean below
Failure to properly terminate the ungrounded (hot) conductors of a multiwire branch circuit to separate phases could cause the grounded (neutral) conductor to become overloaded with excessive neutral current. Conductor overheating decreases insulating material service life, creating the potential for arc-fault fires in hidden locations.
The micro is in the lights circuit, a tap from the cans' light to a GFCI receptacle inside the cabinet and of course the micro acts as a "dimmer switch" for the lights when it start. It is a 1550 watts microwave.
So, I have to disconnect this tap, I cannot tap the SA circuits and the situation is "very expensive" because in the way it was remodeled to bring a new dedicated circuit.
Maybe, (doing a load calculation) tap the kitchen light to the other (s) light circuits and leaving that circuit alone for the micro ...
That sounds like a good plan- just pick up another lighting ckt elsewhere for the kitchen lights
Another option is to tap the dishwasher, disposal or another circuit available, not the SA, but with a 1550 one?
You could also do that- Read 210.23 carefully- you can exceed the 50% rating of the ckt with 2 pieces of equipment fastened in place, provided none of the other items listed are on that ckt.
The seller is an investor and will not put any money into, the expenses have to come from the realtor pocket and I feel bad.
Either you want to get paid or not- no need to feel bad -you have to charge accordingly if you intend to bring it up to code, and somebody has to pick up the tab.