"If the lights/microwave are on an improperly installed MWBC, simply switching #10 or 14 breaker's wire to #12 breaker, to use both legs, may solve the problem"
JFletcher, I don't get the above ...
If a MWBC (eta: of a 120/240V split phase/residential system) has 2 ungrounded (hot) conductors originating from the same leg, the amperage on its neutral will be the sum of the currents, and potentially overloaded. If the ungrounded conductors originate from opposite legs, the amperage on the neutral is the difference in currents and it's impossible to overload the neutral. There'd be less voltage drop as well.
I've no idea how this house is actually wired, the fact that MWBC are on the same leg would make me wanna rip it all out and start over. The lighting doesnt need a dedicated circuit. Yes, it's possible it has been wired that way for 26 years and hasnt burnt down. The NEC is pretty conservative. I wouldnt try to put 30+A on #14 neutral for any amount of time, and perhaps there has never been overcurrent on the neutral.
My apologies, maybe I am confusing thing out. Notice the MWBC, see breakers (2-4), (6-8) and (10-14: same phase) and in (12) a single dark grey #12 in a 15 amps breaker that goes to the kitchen light and where the micro is taped.
You could just put the two ungrounded on opposite lines instead of ripping it out, unless you believe the it has been compromised by overloading or other issues not mentioned are present.
For no longer then many microwaves are loaded at a time I really doubt the neutral has been overloaded enough to cause it much damage either though. Not saying it makes the install correct, but I don't think that neutral is as compromised as it would be with a much more continuous load of same amperage.
Someday that microwave just might be replaced with one with different instructions - if cord already reaches a receptacle is it still the original electricians fault it doesn't comply with the instructions?
Many of us run a individual circuit to such appliance locations regardless of what model may get installed - generally is seen as good practice regardless.
I'm sure one can get away with not running one, but on new installations, many of us "overwire" kitchens as a general rule anyway.Personally, I have never not run a 20 amp individual circuit to an over the range microwave.
Personally, I have never not run a 20 amp individual circuit to an over the range microwave.