starbright28
Senior Member
- Location
- Minnesota
I have this one test question that I'm wondering if I answered correctly or not.
the test question that I had is as follows: you have 2 paralleled 500 kcmil copper conductors going to the service. I don't think they said what the overcurrent protection was, or even if it was in the problem. anyways they were asking the size of the equipment ground needed. (copper)
Here is how I answered. I'm looking for the correct way of figuring this out because i am not sure if I was correct, or not. And if I am not correct then our engineer is not correctly sizing the equipment ground when we have paralleled sets.
My answer: 1/0 from table 250.66. I took the 500kcmil copper condutors to get my size from the chart.
Comments??????
the test question that I had is as follows: you have 2 paralleled 500 kcmil copper conductors going to the service. I don't think they said what the overcurrent protection was, or even if it was in the problem. anyways they were asking the size of the equipment ground needed. (copper)
Here is how I answered. I'm looking for the correct way of figuring this out because i am not sure if I was correct, or not. And if I am not correct then our engineer is not correctly sizing the equipment ground when we have paralleled sets.
My answer: 1/0 from table 250.66. I took the 500kcmil copper condutors to get my size from the chart.
Comments??????