Pex plumbing no copper

Fordean

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
If a building is completely pex tubing Except for 3 inches of copper entering concrete wall from utility Grounding electrode rule ?
 
Are you asking about it being a GE? If it meets the requirements of being a GE per 250.52(A)(1) then you have to use it.
 
Top