F Fordean Senior Member Location New Jersey Occupation Electrical Contractor Today at 2:57 AM #1 If a building is completely pex tubing Except for 3 inches of copper entering concrete wall from utility Grounding electrode rule ?
If a building is completely pex tubing Except for 3 inches of copper entering concrete wall from utility Grounding electrode rule ?
roger Moderator Staff member Location Fl Occupation Retired Electrician Today at 6:29 AM #2 Are you asking about it being a GE? If it meets the requirements of being a GE per 250.52(A)(1) then you have to use it.
Are you asking about it being a GE? If it meets the requirements of being a GE per 250.52(A)(1) then you have to use it.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Today at 7:23 AM #3 Fordean said: Except for 3 inches of copper entering concrete wall Click to expand... If the copper pipe on the other side of the wall buried for at least 10'? Then as Roger stated it's an electrode and must be used as part of the GES.
Fordean said: Except for 3 inches of copper entering concrete wall Click to expand... If the copper pipe on the other side of the wall buried for at least 10'? Then as Roger stated it's an electrode and must be used as part of the GES.