BillK-AZ
- Mesa Arizona
A little off the main thread.
Back in the mid-1990's when Trace Engineering introduced the SW series inverters that were capable of interactive operation with the utility I installed one for a customer in a rural area and the utility was getting it's first experience with these. The utility brought out power quality equipment and could display and quantify the current and voltage waveforms. We observed remarkable differences with the inverter on and off. With the inverter off the voltage waveform was was distorted while the current waveform (residential service) was reasonably clean. When the inverter was on-line things changed, the voltage waveform became clean while the current waveform was highly distorted. This puzzled the utility technician and he was initially not going to approve the connection because of the current distortion. I called the utilities' interconnect manager and he traveled to the site to also observe. The manager approved the installation since he determined that the inverter operation was producing harmonics that offset and corrected the existing situation. The SW inverters are not voltage followers, but rather standalone inverters that synchronize with the grid voltage, phase and frequency, then connect.
I do not know if the same effect is produced by the modern transformer-less inverters. One local utility, SRP, is now deploying special versions of inverters that offer VAR control. No public results yet. Utility scale inverters in Europe have had this capability for a few years.