herding_cats
- Kansas
- Mechanical Engineer
I just started contracting for a new company that does a lot of power factor correction cap banks with harmonic filters, etc. They sent me the data sheets from the manufacturers and install guidelines. What I saw was a major red flag:
Most of these cap banks were installed using the main service lugs either at main breaker or main disconnect because the MDPs were already filled with breakers. In some of these installs, there were connecting #6 wire to the main lugs, like on 400A service, then feeding them out to a disconnect, then to the cap bank. I know of nothing about the connections of cap banks in NEC guidelines, but I sure as hell know about ampacity and branch circuits. I talked to one of the electricians that works for the company that produces these cap banks, and he basically said “we have to do what we need to get them installed” and “cap banks are not considered a load”.
If there is room at the MDP then they do connect to a breaker. If not, they jump on the main lugs or even install “flag” terminals on the main lugs.
If anyone knows about this please respond.
See the cap bank manufacturer rep here:
www.C3Greenenergy.com