Has anyone tried to increase the size of an existing underground service in PG&E territory? (Yes, I have the Greenbook, and yes, I have talked to Service Planning, I'm looking for some practical experience.)
My customer owns one of five houses that are fed from a common vault in the sidewalk. It appears that all 5 houses are fed with 1 1/4 RMC. My customer's house is about 80 - 90 feet from he vault to the service point.
Right now they've got #6 TW in there. I'd like to take the service to 125 amps.
PG&E Service planning is saying, dig us a trench and put a 3" pipe in it and we'd be happy to increase the size of your service.
At least one other house in the vault has #2 THHN in it, so I know that's not original.
All of the service upgrades I've done have either been overheads, or undergrounds that already have #2 to the landing can. I haven't had to deal with this particular issue yet.
My first question is, Is there anyway to get PG&E to pull in new wire in the existing pipe? Or will they let me do it?
My second question is what to do inside the garage if I actually get new conductors in the pipe. The existing Service Lateral terminates in the garage. PG&E wants the meter outside. My idea is to LB from the exiting pipe, out through the wall and mount a landing can, meter, main disconnect out there. From everything I read it is o.k. for the service conductors to come inside the building they serve and then go back outside. Does that sound o.k.?
Thanks as always for your input.
My customer owns one of five houses that are fed from a common vault in the sidewalk. It appears that all 5 houses are fed with 1 1/4 RMC. My customer's house is about 80 - 90 feet from he vault to the service point.
Right now they've got #6 TW in there. I'd like to take the service to 125 amps.
PG&E Service planning is saying, dig us a trench and put a 3" pipe in it and we'd be happy to increase the size of your service.
At least one other house in the vault has #2 THHN in it, so I know that's not original.
All of the service upgrades I've done have either been overheads, or undergrounds that already have #2 to the landing can. I haven't had to deal with this particular issue yet.
My first question is, Is there anyway to get PG&E to pull in new wire in the existing pipe? Or will they let me do it?
My second question is what to do inside the garage if I actually get new conductors in the pipe. The existing Service Lateral terminates in the garage. PG&E wants the meter outside. My idea is to LB from the exiting pipe, out through the wall and mount a landing can, meter, main disconnect out there. From everything I read it is o.k. for the service conductors to come inside the building they serve and then go back outside. Does that sound o.k.?
Thanks as always for your input.