hillbilly1
Senior Member
- Location
- North Georgia mountains
- Occupation
- Owner/electrical contractor
How many times have we ran a 4” conduit for AT&T to put in a cable smaller than your pinky? And that was before fiber! LOL!
This is a panel upgrade from 125 to 200A that currently has 2" stubbed up thru the foundation. Replacing this with a 3" will require the foundation to be enlarged, basically a ton of extra work. Any suggestions as to how to convince PG&E to let me use 2" as I have done on other panel upgrades?
Upgraded Panel
13. For upgraded panels where the new specified size of service conductor will fit in the existing conduit, it is not
necessary to upgrade the conduit to the currently specified size for the new panel if both of the following are met:
A. The maximum fill ratio is not exceeded.
B. The calculated cable pulling tensions along the conduit route is within limits of the new cable.
Good catch kwired a U-125 does only accept a #6 as the smallest, however incase anyone is reading this doing a 30A 120V service for a traffic light or gate a B-Line 011 125A Meter takes #14 - 2/0. But were off topic....../...You probably still will need 6 AWG load side conductors in the meter because that is likely as small of a conductor it will accept.
Because it does not matter if it passed inspection, if it does not meet their requirements it is not getting connectedHow can a POCO require a raceway that is to large for the enclosure?
Maybe I'm a little slow but I don't understand how you can have rule that can't be complied with when using a 200 amp meter socket or meter/main that is not deep enough to allow a 3" raceway. I can't recall any that are deep enough to do this.Because the CPUC allows them to set their own rules.
Maybe I'm a little slow but I don't understand how you can have rule that can't be complied with when using a 200 amp meter socket or meter/main that is not deep enough to allow a 3" raceway. I can't recall any that are deep enough to do this.
They do exist, the local poco requires a three inch stubbed down for 200 amp ug services. The harder ones to find are meter/main combos.Maybe I'm a little slow but I don't understand how you can have rule that can't be complied with when using a 200 amp meter socket or meter/main that is not deep enough to allow a 3" raceway. I can't recall any that are deep enough to do this.
Good to know. Never seen 'em that deep.Here is a Square D meter main combo that has up to 3” ko.
How can a POCO require a raceway that is to large for the enclosure?
This is interesting info. I used to work in an area that uses the EUSERC standard but it has been a while. Do you know when the standard changed to require 3" for 200 amp services? I just looked at this POCOs latest service book and you are correct that EUSERC now requires this.PG&E has strict requirements (they follow EUSERC) for the size of the pull section where underground services enter and terminate. Anything that meets their requirements will be large enough for a 3" raceway. You can not terminate an underground service in a standard meter socket.
Edited to add:
The panel in the link above does not meet EUSERC requirements for underground services and would not be allowed.
I don't remember exactly when the minimum was changed to 3" but it has been at least 20 years. When the requirement first started some of the underground inspectors would allow swedge reducers at the building so a 2" 90 and stub could be used in the wall.This is interesting info. I used to work in an area that uses the EUSERC standard but it has been a while. Do you know when the standard changed to require 3" for 200 amp services? I just looked at this POCOs latest service book and you are correct that EUSERC now requires this.