I made a rookie mistake while i was doing an estimate walk-through for a friend.
he wanted to hook up a machine at 240v that included a big load coil, and a small conveyor motor.
I was told a previous tenant in the same building was running a 240v air compressor out of the panel
that the client had shown me.
The panel tested 240v between legs so i told him it was what he thought.
i acquired the job specs from him:
the machine is scheduled to be on for many hours at a time
The machine requires 22A fed by two phases of 120v equaling 240v, and has a twist lock plug.
I sized it for 30A on a standard two pole breaker,
running (x1)#12 ground and (x2)#8 conductors going through about 75 feet of 3/4 EMT to the panel.
i installed the circuit and went to test the socket before anything was to take power from it.
It was reading 240v from phase to phase, then it read 240v phase to ground.
I inspected the panel and found 1 of the 3 legs with 0 potential to ground.
I set my breaker to the live legs and plugged the machine in.
it did not start.
Now i am here,
knowing now that i'm dealing with a corner grounded 240v Delta system, the wrong type of breaker,
and having only this panel to work with.
My Questions:
1. if i use (x2) single phase 2 kva (pri 480v/240v-240v/120v sec) transformers, will it work, and if so,
will the phase's angular difference cause more wear on the machine than 2 phases 180* apart?
2. hypothetically, if i wanted to take the output of those transformers(120v and 120* out of step) and balance the phases 180* out of step, would i be able to use the grounded b phase through a third transformer and use it like an isolated ground?
reason being that while Vab|Vag=0*, Vcb=60*, Vca=120* and Vcg=-120*.
connection at machine
--------------
A phase
C phase
b(isolated ground)
he wanted to hook up a machine at 240v that included a big load coil, and a small conveyor motor.
I was told a previous tenant in the same building was running a 240v air compressor out of the panel
that the client had shown me.
The panel tested 240v between legs so i told him it was what he thought.
i acquired the job specs from him:
the machine is scheduled to be on for many hours at a time
The machine requires 22A fed by two phases of 120v equaling 240v, and has a twist lock plug.
I sized it for 30A on a standard two pole breaker,
running (x1)#12 ground and (x2)#8 conductors going through about 75 feet of 3/4 EMT to the panel.
i installed the circuit and went to test the socket before anything was to take power from it.
It was reading 240v from phase to phase, then it read 240v phase to ground.
I inspected the panel and found 1 of the 3 legs with 0 potential to ground.
I set my breaker to the live legs and plugged the machine in.
it did not start.
Now i am here,
knowing now that i'm dealing with a corner grounded 240v Delta system, the wrong type of breaker,
and having only this panel to work with.
My Questions:
1. if i use (x2) single phase 2 kva (pri 480v/240v-240v/120v sec) transformers, will it work, and if so,
will the phase's angular difference cause more wear on the machine than 2 phases 180* apart?
2. hypothetically, if i wanted to take the output of those transformers(120v and 120* out of step) and balance the phases 180* out of step, would i be able to use the grounded b phase through a third transformer and use it like an isolated ground?
reason being that while Vab|Vag=0*, Vcb=60*, Vca=120* and Vcg=-120*.
connection at machine
--------------
A phase
C phase
b(isolated ground)