I've got a job that has a 3 phase 3w 240v corner grounded delta service. This service takes care of two air cond loads. On site there is a 3 phase 4w 120/240 genset and xfer switch. If I install a seperate xfer switch fed from the same genset, is there any way to comply with the code and feed the 3 phase 3w corner grounded load with the 120/240 3 phase 4w generator? I know that the A/C equipment will run but how would the grounded/ungrounded phase be marked to identify which system its running on. Also would this installation not comply with 200.11 ?
Thanks