Hello first time posting here, that I can remember at least. Looong post.
I am an hvacr Tech and I have a question on a 3-phase Chiller and pump being powered by a roto phase. What I've always understood as far as supplied voltage and voltage under load, I should be within or less than 2% deviation. I usually get this by adding the three voltages dividing by 3 and then calculating how far off the farthest one is from that. So what I have on this phase converter is 275 254 + 240 volts when the 208-230 3 phase pump motor starts at 3 horsepower. All phase converter capacitors connected. I will read 9.8 amps 7.7 and 7.7. F L A is 8.4.
Now my understanding is that never should I have a motor running with any leg over FLA , but the phase converter manufacturer says that is fine, the motor supplier says that is fine. However if I read information from Fluke or US Motors, or another phase converter manufacturer, they all say that is not o.k.
So the phase converter manufacturer said to disconnect a few of the Run capacitors , to drop the voltage , and that would steady out the amps and bring them lower. The amps did not drop they actually went to 5, 8, 9.8. At new voltages of 235, 235, 246. 3% deviation.
The chiller itself, (when running one of the 4 compressors) the amps on it run 30-27 and 13 at 3% voltage deviation.
Another thing that I have read is a 3% voltage deviation can result in 50% reduction of motor life due to insulation over-heat.
Both amp draws deviate by 40%! 10% is allowable.
I'll bet you want more specific equipment info but I don't have that right now. Site is 3 hours away.
I could get more from others tho.
I'd love to know what you guys say about this. Maybe just more generic input about deviation.
Thanks
PS....the chiller startup manual calls for less than 2% voltage deviation.
Sent from my SM-G930V using Tapatalk
I am an hvacr Tech and I have a question on a 3-phase Chiller and pump being powered by a roto phase. What I've always understood as far as supplied voltage and voltage under load, I should be within or less than 2% deviation. I usually get this by adding the three voltages dividing by 3 and then calculating how far off the farthest one is from that. So what I have on this phase converter is 275 254 + 240 volts when the 208-230 3 phase pump motor starts at 3 horsepower. All phase converter capacitors connected. I will read 9.8 amps 7.7 and 7.7. F L A is 8.4.
Now my understanding is that never should I have a motor running with any leg over FLA , but the phase converter manufacturer says that is fine, the motor supplier says that is fine. However if I read information from Fluke or US Motors, or another phase converter manufacturer, they all say that is not o.k.
So the phase converter manufacturer said to disconnect a few of the Run capacitors , to drop the voltage , and that would steady out the amps and bring them lower. The amps did not drop they actually went to 5, 8, 9.8. At new voltages of 235, 235, 246. 3% deviation.
The chiller itself, (when running one of the 4 compressors) the amps on it run 30-27 and 13 at 3% voltage deviation.
Another thing that I have read is a 3% voltage deviation can result in 50% reduction of motor life due to insulation over-heat.
Both amp draws deviate by 40%! 10% is allowable.
I'll bet you want more specific equipment info but I don't have that right now. Site is 3 hours away.
I could get more from others tho.
I'd love to know what you guys say about this. Maybe just more generic input about deviation.
Thanks
PS....the chiller startup manual calls for less than 2% voltage deviation.