A HVAC tech is dealing with a 'phase loss' issue on a 208V compressor but when I go out to check all phases are present, its a older rooftop unit and it looks as if the disconnect was replaced recently but not by me.
There is a heatwave going on and the incoming utility voltage is about 198 per phase today, L-N 114 at the service and at the load terminals of the breaker (3-P 60) its a 208/120 building.
However up on the roof I am getting L1-L2 187, L2-L3 180 L3-L1 180 and 14- 60V Line to ground screw ( no ground wire in the conduit on the roof ). When the HVAC tech manually started a motor L2 - L3 start dropping fast, L1-L2 fluctuate but not much.
Any advise is appreciated