JustCallBen
Member
- Location
- San Diego
- Occupation
- Building contractor
I have a client car wash that has a 277/480 Wye service. They have experienced significant equipment losses over the past 6 years due to brownouts, phase losses and the like. There may have been surges but there is no hard data to back that up. Of course, the utility claims no blame or knowledge every time.
The most recent incident was a phase loss due to a defective fuse at the transformer on the pole. I was there when the lineman changed it out and I gave the old fuse to the customer for evidence. The lost phase then caused burn out of the coils of 8 contactors probably due to faulty voltage from the in-house 120/240 transformers. One motor was lost but not sure if it was due to the phase loss as it was pretty crusty to begin with.
Anywho, I would like to provide phase loss protection for the main service and for a 100A MCC downstream from that. What equipment would you recommend?
I've looked at shunt trip but it seems like most of them are not really focused on my application as they require an energized circuit to shunt. What if the phase that I need to shunt is the one that is lost?
The most recent incident was a phase loss due to a defective fuse at the transformer on the pole. I was there when the lineman changed it out and I gave the old fuse to the customer for evidence. The lost phase then caused burn out of the coils of 8 contactors probably due to faulty voltage from the in-house 120/240 transformers. One motor was lost but not sure if it was due to the phase loss as it was pretty crusty to begin with.
Anywho, I would like to provide phase loss protection for the main service and for a 100A MCC downstream from that. What equipment would you recommend?
I've looked at shunt trip but it seems like most of them are not really focused on my application as they require an energized circuit to shunt. What if the phase that I need to shunt is the one that is lost?