Just came back from a new client meeting. A school in the boonies is being hammered by single plasing on the distribution line serving the school. As a result they are loosing motors. Obviously, they need phase loss protection. It's affecting not just three phase motors, but also the room AC units so individual protection is not the answer.
They want to simply trip the main and manually reset the breaker. I have no problem with that. They have radio communication with the school to central monitoring that will tell them to go and reset the main.
Fortunately they have a 1600A main at 480V with GFIC. So it already has a shunt trip on the main disconnect. Sometimes you lick out.
I plan on installing a phase loss sensor to monitor the incoming line and trip the main as needed. One of the TimeMark ice cube units.
However, my brain went into details and I see the need for a time delay before tripping to avoid nuisance trips.
Several questions for the forum:
1. How long a time delay? I was figuring on 3-5 seconds. Obviously I will use a pneumatic relay since I need to time out upon loss of power.
2. A concern is the source for trip power to the shunt trip. I will be getting with GE for a wiring diagram for the GFIC circuit. If the phase that's lost is on the leg I am getting the power to hit the shunt trip, will there be enough voltage to trip the shunt trip? There is a CPT to go from 480V to 120V.
Anybody run into this?
Thanks ahead of time,
RC
They want to simply trip the main and manually reset the breaker. I have no problem with that. They have radio communication with the school to central monitoring that will tell them to go and reset the main.
Fortunately they have a 1600A main at 480V with GFIC. So it already has a shunt trip on the main disconnect. Sometimes you lick out.
I plan on installing a phase loss sensor to monitor the incoming line and trip the main as needed. One of the TimeMark ice cube units.
However, my brain went into details and I see the need for a time delay before tripping to avoid nuisance trips.
Several questions for the forum:
1. How long a time delay? I was figuring on 3-5 seconds. Obviously I will use a pneumatic relay since I need to time out upon loss of power.
2. A concern is the source for trip power to the shunt trip. I will be getting with GE for a wiring diagram for the GFIC circuit. If the phase that's lost is on the leg I am getting the power to hit the shunt trip, will there be enough voltage to trip the shunt trip? There is a CPT to go from 480V to 120V.
Anybody run into this?
Thanks ahead of time,
RC